SignalExpress
Flow Meter
I am using Signal Express and  a usb-6000 DAQ, I am measuring flow from a flow meter and need to configure a totalizer in signal express so I can track how much flow we have going out of the plant. I also need to configure instantaneous flow at a point and time when I take samples. Any Ideas.
(5,648 Views)
Hi joecoffman,
Have you worked with SignalExpress before and have you started a project already for your totalizer?
The introduction on how to start configuring a project can be found on page 14 of the pdf below:
http://www.ni.com/pdf/manuals/373873h.pdf
Alex
Hardware Engineer
(5,618 Views)
I have a little knowledge of SignalExpress, mostly what I have self taught reading and online videos. I am able to acquire my signal with DAQmx and set up steps as to min, max, average in current. I am how ever unable to get 0-5 volt scaled appropriately (0= no flow, 5=1600 gpm) and then figure how to translate that to total flow over a 24 hour period.
(5,613 Views)
In order to scale the voltage properly, you will need to create a custom linear scale:
How to Create a Custom Scale in SignalExpress
https://knowledge.ni.com/KnowledgeArticleDetails?id=kA00Z000000P9SeSAK
How often do you take samples of flow rate?
Alex
Hardware Engineer
(5,610 Views)
OK I got the Custom Scale set up and works perfectly.
Now I just need to set up the Total flow for a 24 hour period.
I sample 3 times a day.
(5,605 Views)
Glad to hear the scale is set up correctly.
Since you're sampling 3 times per day, that means each sample represents 8 hour increments correct?
Each sample would be the average flow for that 8hr period, so total flow be the summation of the 3 sample values multiplied by 8 by 60(min):
Total = 8*60(sample1+sample2+sample3)
Alex
Hardware Engineer
(5,591 Views)
