joecoffman
Member

Flow Meter

I am using Signal Express and  a usb-6000 DAQ, I am measuring flow from a flow meter and need to configure a totalizer in signal express so I can track how much flow we have going out of the plant. I also need to configure instantaneous flow at a point and time when I take samples. Any Ideas.

5 REPLIES 5
algarcia
NI Employee (retired)

Re: Flow Meter

Message contains a hyperlink

Hi joecoffman,

 

Have you worked with SignalExpress before and have you started a project already for your totalizer?

 

The introduction on how to start configuring a project can be found on page 14 of the pdf below:

http://www.ni.com/pdf/manuals/373873h.pdf

Alex
Hardware Engineer
joecoffman
Member

Re: Flow Meter

I have a little knowledge of SignalExpress, mostly what I have self taught reading and online videos. I am able to acquire my signal with DAQmx and set up steps as to min, max, average in current. I am how ever unable to get 0-5 volt scaled appropriately (0= no flow, 5=1600 gpm) and then figure how to translate that to total flow over a 24 hour period.

algarcia
NI Employee (retired)

Re: Flow Meter

Message contains a hyperlink

In order to scale the voltage properly, you will need to create a custom linear scale:

How to Create a Custom Scale in SignalExpress

https://knowledge.ni.com/KnowledgeArticleDetails?id=kA00Z000000P9SeSAK

 

How often do you take samples of flow rate?

Alex
Hardware Engineer
joecoffman
Member

Re: Flow Meter

Message contains a hyperlink

@algarcia wrote:

In order to scale the voltage properly, you will need to create a custom linear scale:

How to Create a Custom Scale in SignalExpress

https://knowledge.ni.com/KnowledgeArticleDetails?id=kA00Z000000P9SeSAK

 

How often do you take samples of flow rate?


OK I got the Custom Scale set up and works perfectly.

Now I just need to set up the Total flow for a 24 hour period.

 

I sample 3 times a day.

algarcia
NI Employee (retired)

Re: Flow Meter

Glad to hear the scale is set up correctly. 

Since you're sampling 3 times per day, that means each sample represents 8 hour increments correct?

 

Each sample would be the average flow for that 8hr period, so total flow be the summation of the 3 sample values multiplied by 8 by 60(min):

Total = 8*60(sample1+sample2+sample3) 

Alex
Hardware Engineer