Lookout
Modbus Com driver lost after timeout
LO 6.6 running on Win XP
We have 5 RTUs running over a slow radio linkage.  All works OK until there is a radio timeout or other com glitch. The modbus begins normal polls and sometimes recovers OK, however other times, it begins sending junk and never recovers.  Only a LO restart clears the problem.  An example trace is attached, but here is the last few
10:24:31.3 - Modbus1 ->
[3C][04][00][00][00][03][B4][E6]
10:24:36.5 - Modbus1 <-
[3C][04][06][2B][2B][69][EA][15][96][FC][89]
10:25:04.1 - Modbus5 ->
[40][02][00][00][00][05][B7][18]
10:25:30.7 - Modbus5 ->
Here...each of the 5 RTUs are polled, then the following starts:
10:32:41.3 - Modbus5 ->
[3A][34][30][30][32][30][30][30][30][30][30][30][35][42][39][0D][0A]
10:32:49.2 - Modbus5 ->
10:32:57.0 - Modbus5 ->
10:33:04.8 - Modbus5 ->
10:33:12.6 - Modbus5 ->
10:33:20.5 - Modbus5 ->
10:33:28.3 - Modbus5 ->
10:33:36.1 - Modbus5 ->
10:33:44.0 - Modbus5 ->
This continues until LO is restarted, then everything is OK.
Why is the Modbus driver sending this garbage message: [3A][34][30][30][32][30][30][30][30][30][30][30][35][42][39][0D][0A]
It looks like ASCII text with a LF/CR at the end, like a modem init string.  Our COM line is hardwired, no modem is involved.
Thanks in advance.
(5,739 Views)
It isn't garbage. It is Modbus Ascii. Lookout will attempt to poll in Ascii mode if RTU mode fails.
You can disable this behaviour by setting up a modbus.ini file that contains the text Protocol = RTU.
Search the NI site for more info on the .ini files.
Bob
(5,730 Views)
(5,720 Views)
