01-22-2020 11:42 AM
Some EtherCAT devices have 3 rotary switches that you can use to set the device address. How do I find out what this address is from LabVIEW? I know if you daisy chain ethercat devices then the device number that shows up in LabVIEW is the order of the network connection. I'm not asking for that. This is a fixed address assigned by using the physical switches. I'm assuming there is an ethercat spec for defining this in an SDO somewhere.
解決済! 解決策の投稿を見る。
02-04-2020 05:09 PM
I believe it's the "position address" property that you can read when you wire in an EtherCAT slave vairable to a property node. I believe you can drag the variable from the project or discover programmatically
02-05-2021 11:44 AM
No, I'm already aware of that property. This "position address" is not the one I'm looking for. That lists the address assigned to the device by the NI ECAT driver after it scans the network, which is different. For example, if you have 3 devices daisy-chained. Then the addresses are 1,2,3 (or 0,1,2).
03-02-2021 04:17 PM
To follow-up on this. I got a response from NI support. They claim that this feature is only required by FSoE (Functional Safety Over Ethercat). Their hardware doesn't support this ETG spec so therefore they cannot read the hardware ID. It would be nice for NI to support this capability as it's becoming more popular in industrial automation.
