NI Labs Discussions
NI LabVIEW Modbus API Discussion
The "Set Unit ID" will be ignored when using Modbus TCP (check the "Context Help" of the method).
Have you created a separate TCP-connection for each of the Eurotherm 3504 devices?
______________________________________________
Marcus Törndahl (System Architect)
Message 431 of 529
(3,482 Views)
I have only one eurotherm and thus one tcp connection for it.
Currently, I can communicate with the module, but every so often the connection is dropped for some reason.
Message 432 of 529
(3,480 Views)
Is there a limit on how often the application can read values from the Eurotherm 3504 device? Do you have a programmers manual for the device?
Message 433 of 529
(3,468 Views)
There must be a limit, I haven't found it in the manual, the manual itself is very scarce about communication. On the other hand, the problem occurs even at slow acquisition rates.
Right I have bypassed the problem by ignoring the error and resetting the communication when I detect one, but this is not really ideal and reliable. I'd like to get something more robust.
Message 434 of 529
(3,463 Views)
Hi Supreeth.K
In fact, it was my mistake regarding the tcp connection. I have connected it properly to test the eurotherm.
Then, on a single read, the communication works, it just drops out every so often.
And I am aware that when the eurotherm is in config, it drops the communication. There is also no watchdog activated on the eurotherm in the current configuration.
Matthieu
Message 435 of 529
(3,457 Views)
Marcus and Supreeth,
Thanks for your help, I think I found the problem. I said that the computer had two ethernet cards (realtek PCIe GBE familly controllers), which offers a nice feature of giving access to both an internal and an external network, with one configured with a fixed IP and the other on DHCP. I found online some people complaining about issues of connections with those cards. I thus tried with an external USB ethernet card and I've run it all weekend long without any error coming out. So I suppose there is some kind of interference between the two cards.
Thanks for your help again,
Matthieu
Message 436 of 529
(3,422 Views)
Is there any way to read out the raw incomming modbus commands somewhere in this library?
Regards
Mrmas
Message 437 of 529
(3,312 Views)
I'm curious if anyone else has run into the error I linked. I've searched on this forum, as well as abroad to see if this is a Modbus TCP specific error. I haven't found any info anywhere that has been super helpful.
The issue is when I try to read a holding parameter from my device more than 255 times. I have no issues communicating with the device, but if I loop the "read holding registers.vi" it will give me this error after 255 times. Is there a buffer somewhere that needs to be cleared out? I have tried reading for example 10 times and then using the Shutdown vi to close the connection. If I reopen a connection to the same device and continue reading after 255 times it will fault out no matter what. Is there something else I need to do to properly close the connection? I haven't found any documentation from the manufacturer on this matter either.
Message 438 of 529
(3,126 Views)
Hi ,
Not sure what the root cause of your error is.
I tried your VI with one of my modbus clients and there were no errors (despite running upto 400 times). So I dont think there is anything wrong with your VI (or the LV modbus API).
Try to replace your input tunnel (at the for loop) for your modbus connection reference with a shift register and see if it makes any difference.
Thanks and Regards,
Supreeth.K
Message 439 of 529
(3,104 Views)
Thanks for the suggestion, I'll give that a shot and see if it helps.
I did play with the loop speeds, as this needs to be a read rate of (50-100ms). Running Wireshark while polling it looks like there were some connection issues at the 50ms mark. Looks like I may just have to slow the reading down as much as the application will allow.
Message 440 of 529
(3,100 Views)
