07-15-2010
02:06 AM
- last edited on
02-10-2025
05:10 PM
by
Content Cleaner
Hi everyone !
I need to build an application with Labview with HMI etc...and I also need to control 3 solenoid valves.
I have the choice for the type and I was thinking of using those one :
SMC VT307 with 24Vdc power consumption 5W
To control them I identified :
cRIO-9481 with USB-9162
Is this a good choice ? Because I'm wondering if this USB device can give enough power to control the valves, as I don't see any external power supply on the USB device ?
If you think about a better choice, your proposal will be welcome.
Thanks for all in advance.
07-15-2010 07:07 AM - edited 07-15-2010 07:08 AM
All it needs more is a 24V powersupply.
You should choose solenoid valves with a build in snubber circuit or free running diode to protect the relays from the turn off spark you get when turning off an inductive load.
This protection will increase the turn off time (some ms) of the valve (just in case that this matter 😉 )
07-15-2010
07:20 AM
- last edited on
02-10-2025
05:10 PM
by
Content Cleaner
Turn off time is not really important.
I want to build something as simple as possible.
So sorry Henrik Volkers but I don't really understand if the hardware I have selected is suitable to control those valves ?
The 24V will be provide by the cRIO-9481 with USB-9162 without external power supply ?
Sorry I'm not really familiar with the hardware.
Thanks again
07-15-2010 09:12 AM
You will need a seperate 24VDC power supply to power the solenoid.
07-15-2010 09:47 AM
Ok
So basically what is the schematic ?
3 CHa of the NI 9481 are connected to the 24V power supply positive
3 CHb go to the positive of the solenoid valves
Negative of solenoid valve to the negative of the power supply.
Does the negative need to be connected to the NI 9481 somewhere as well ?
And about the power supply, I have one here which is 24V, 2.5A is there a limit to not arm the NI device ?
Thanks again guys it helps a lot
07-15-2010 10:08 AM
You will wire the 24VDC power supply so that the ground is connedted to the solenoid ground and the 24Vdc is wired throught he relay module. The relay module should provide protection for the DAQ system. I usually try to electronically isolate my solenoids from my system so I do not see spicks back through when I am measuring something with a sensor. If you are not measuring something then it probably is not a problem.
07-15-2010 10:16 AM
Ok, so what I wrote above was finally correct ![]()
No I don't need to measure.
I think I have my setup.
I will order the NI devices.
Thank you
06-08-2011 02:24 PM
Can the NI PS-17 Power Supply be used for the solenoid valve power? Thanks!!
06-09-2011 08:58 AM
I would expect that would be big enought to power most anything that you want to run. You need to look at the power consumption for the solenoids that you are looking to control and add it up. You could probably get a smaller and cheaper power supply somewhere else. Accopain, Rhino, Analog Devices or any other power supplier.
Do the homework and the math and get what you need not what is avaliable through NI.
06-09-2011 02:36 PM
Thanks, one more question though, I don't need the extra power supply if I use a 120 VAC solenoid valve and draw power from mains, right? Thanks!!
Andy
