Sampling rate

I have a question about sampling rate. I have a program where I need to take measurement every 1 millisecond from a channel (10 samples in every 1  millisecond). So correct me if I am wrong.  Under the DAQmx timing, The sampling rate I set it as 10,000. The number of samples per channel I set it as 10. So the while loop will cycle every 1 millisecond and take 10 samples and gives a total sample of 10,000 per second. 

 

thank you. 

0 Kudos
Message 1 of 15
(3,317 Views)

That sounds correct. What exactly is the question? Have you tried it?

Message 2 of 15
(3,295 Views)

Thanks for the reply. I needed some validation from the experts here about my theory on sampling rate. 

Sorry I posted the question in a confusing way. All I want to do is to get values( at least 10 samples)  from a sensor on every 1 milli second. 

0 Kudos
Message 3 of 15
(3,289 Views)

@realbasil wrote:

I have a question about sampling rate. I have a program where I need to take measurement every 1 millisecond from a channel (10 samples in every 1  millisecond). So correct me if I am wrong.  Under the DAQmx timing, The sampling rate I set it as 10,000. The number of samples per channel I set it as 10. So the while loop will cycle every 1 millisecond and take 10 samples and gives a total sample of 10,000 per second. 

 

thank you. 


Is there a reason you need to get the samples every 1 ms; the overhead in calling that will likely make your VI time out. 100ms interval is a good choice, I would not try to access much less than 20-50ms, if absolutely needed.

 

mcduff

Message 4 of 15
(3,283 Views)

Mcduff

That is worrying for me. 

Yes, I need to look at the data in the interval of 1ms. The whole test last only 4 seconds. The pass/fail can depend on the value in 1 ms.  

0 Kudos
Message 5 of 15
(3,269 Views)

@realbasil wrote:

Mcduff

That is worrying for me. 

Yes, I need to look at the data in the interval of 1ms. The whole test last only 4 seconds. The pass/fail can depend on the value in 1 ms.  


What device are you using? If a USB Device, the latency will probably make this impossible.

 

For something like this you probably need a FPGA and a Real Time OS to handle a small interval.

 

What are you trying to measure?

 

mcduff

 

 

Message 6 of 15
(3,253 Views)

@mcduff wrote:

Is there a reason you need to get the samples every 1 ms; the overhead in calling that will likely make your VI time out. 100ms interval is a good choice, I would not try to access much less than 20-50ms, if absolutely needed.

Fully agree with the sentiment, but have been known to push the limits to 10 msec and less on *VERY RARE* occasions.

 

That said, I've seen many, many, many (many, many, many, many) threads from new and new-ish users who *think* they need really fast software loop iterations but who really need a more thorough understanding of their DAQ hardware & driver capabilities and a more realistic assessment of what they're looking to accomplish.

 

So what is it that *you* are doing here that would justify a need for a 1 kHz loop rate?  Spoiler: even if you have a legit need, I would not bet on fully satisfying it under Windows.

 

 

-Kevin P

ALERT! LabVIEW's subscription-only policy came to an end (finally!). Unfortunately, pricing favors the captured and committed over new adopters -- so tread carefully.
0 Kudos
Message 7 of 15
(3,251 Views)

I am using cDAQ9185 and 9203 chassis. I am trying to measure the position. 

Thanks for the suggestions, I have to do more research on FPGA and Real time. 

0 Kudos
Message 8 of 15
(3,245 Views)

Do you have to look at the data in real time?  Can you capture more than what's needed (and at a larger chunk/slower measuring rate) and evaluate the data after the test, or is it such that in 10 ms it could crash into something?

Bill
CLD
(Mid-Level minion.)
My support system ensures that I don't look totally incompetent.
Proud to say that I've progressed beyond knowing just enough to be dangerous. I now know enough to know that I have no clue about anything at all.
Humble author of the CLAD Nugget.
Message 9 of 15
(3,230 Views)

You can *measure* with much more manageable loop iteration rates such as 10 Hz (100 msec).  This still lets you display and present data that's as close to real-time as human perception can distinguish.

 

It's only when you need code-based automatic *control* that you *might* need faster loop rates for decision-making and output generation.

 

So are you reacting and controlling something that needs near-instantaneous response or are you merely measuring?   If merely measuring (and that's all you mentioned), then it's highly doubtful you actually need loop iteration rates anywhere near 1 kHz speed.

 

 

-Kevin P