Hi All,
I have a LabVIEW Real-Time executable which I have deployed and is running on a cFP-2220, and now I want to access the front panel of that executable from a local computer connected to it. I am trying to do this by running a VI on the local computer which uses the "RP.Open Connection To Server" VI. I used a similar setup with a cFP and LabVIEW 8.5 and it worked great. I have gone through lots of documentation on the NI site on how to set it up, and have done all the usual things:
I have the VI in a project deployed onto the cFP.
I have enabled the web server and VI server on the target.
I am passing the correct VI name, IP address and port to RP.Open Connection To Server
I can verify that the RT executable is running on the cFP when I deploy it. My problem occurs when I initiate the call to RP.Open Connection To Server, the VI executes the call, but the front panel of the RT executable on the cFP never opens, and I never receive an error from the calling VI (I have an error out from the RP VI to both a dialog and indicator, and I get nothing). It calls the RP VI, but then waits indefinitely and never opens the Front Panel of the RT executable. This exact same problem occurs when I try to make the remote front panel using the web publishing tool, or when I use the "Connect To Remote Front Panel" option in LabVIEW.
Has anyone ever seen this before, or know of anything I might be doing wrong? Is this a problem with 8.6?
Thanks.
Solved! Go to Solution.
12-01-2008 04:19 PM
Hi,
Are you using FieldPoint 6.0.2? We have a Corrective Action Report (#125870) for the remote front panels for the cFP-2220 with LabVIEW 8.6 and FieldPoint 6.0.2. R&D is currently working on a fix, until then, the only known workaround is to using LabVIEW 8.5.1.
12-02-2008 09:50 PM
12-03-2008 12:54 PM
12-03-2008 10:31 PM