Tom,
Has the controller ever worked properly? Using FTP, look at the NI-RT/STARTUP folder (type ftp://x.x.x.x/ni-rt/startup in Internet Explorer, where x.x.x.x is the controller's IP address). What is there?
The LED blinking is documented in the
PXI-8140RT Series User Manual on page B-1. It says:
The USER1 LED indicates LabVIEW RT status:
• If this LED blinks one time every 2–3 seconds, the IP address is 0.0.0.0 (the device is unconfigured).
• If this LED blinks two times every 2–3 seconds, the software on the PXI-8140RT is corrupt or missing, and the box is in safe mode. (Reinstall the software from MAX.)
•
If this LED blinks three times every 2–3 seconds, you have flipped the safe mode switch, causing the box to go into safe mode regardless of whether it could otherwise boot.
Obviously what you are seeing is not documented there...How long does it take to blink 18 times?
We can start from scratch by uninstalling the software on the controller and reinstalling it. To uninstall it, manually put the controller in SAFE MODE (switch S2 - see the PXI-8140RT Series User Manual pp.2-6 and B-2 for details). Right now, booting with S2 switched uninstalls the software. Put the switch back to normal and then reconfigure the controller.
What IP settings are you giving the controller? What version of LabVIEW Real-Time are you using? Which drivers are you putting on the controller? What are the IP settings of the host PC? What is in the program you are using? Are you calling any C code or DLLs?
Regards,
Chad H.
Applications Engineering
National Instruments
http://www.ni
.com/ask