Labview VI using modbus tcp/ip connected to a data acquisition module adam 6017

Solved!
Go to solution

Hi

 

I would like to ask why do I have Error 59 on my program. The data acquisition module is connected to my laptop when I used the adam utility software. However, when I tried to use labview, error 59 occurs and no readings are collected. Where did I make a mistake? 

 

Help is greatly appreciated, thank you!

 

2019-11-12 (2).png is an image of my block diagram.

2019-11-12 (3).png is an image of my front panel.

2019-11-12 (4).PNG is an image showing the data acquisition is connected to by laptop via a ethernet cable.

0 Kudos
Message 1 of 3
(1,974 Views)
Solution
Accepted by ace2light

Error 59 is that the network is down.

 

Your one picture with the working programming shows you are communicating with a device at 10.0.0.11.

Your picture with the non-working VI shows an IP address of 169.254.21.119.

 

Do you think that might the cause of your problem?

0 Kudos
Message 2 of 3
(1,963 Views)

Hi 

 

thank you for your help, greatly appreciated! yeah, it is because of my ip address. 

0 Kudos
Message 3 of 3
(1,943 Views)