Hi all, i am trying to write a First Order Plus Dead Time system into the mathscript, unfortunetaly i found that it appear an error (please refer to the attachements), do anyone have idea or approach to write an FOPDT Transfer function in mathscript? 

Thankyou veery much.

 

0 件の賞賛
メッセージ1/14
6,591件の閲覧回数

Yuki

 

You have to substitute the function:

 

plant = tf(num,den,'inputdelay',0.06)

 

with

 

Gp=set(plant,'inputdelay',0.06);

 

This will set the input delay for the transfer function model. The third argument for the tf command is used to set 'discrete' system with its sampling time. So, the whole script should be:

 

s=tf('s');

num=58;

den=0.33*s+1;

Gp =num/den;

Gp =set(plant,'inputdelay',0.06);

contr = Kp*(1/Ti*s);

sys_cl=feedback (contr*Gp,1);

 

hope this helps

Barp - Control, Simulation, RTT and HIL - National Instruments
0 件の賞賛
メッセージ2/14
6,540件の閲覧回数
解決策
トピック作成者YukiWongが受理

One more thing... this could be easier if you go 100% graphical... スマイリー ハッピー

 

This below is a snippet and you can just drag and drop in your LabVIEW 2011 block diagram and this will copy this code into it.

 

CreateFODwithPID.png

Barp - Control, Simulation, RTT and HIL - National Instruments
0 件の賞賛
メッセージ3/14
6,538件の閲覧回数

Thank you very much barp, both method work for me, but now i had face another problem.

I had try your method and design the PI controller, but the result (overshoot) is different compare to the result (overshoot) by using Matlab.

I had try to copy and paste the code from the Mathscript to the Matlab and step plot it. Consequently, the overshoot shown different value. 

I also had try to check all the value and i found that everything is ok until the last line sys_cl=feedback(Gf,1), Labview has given the answer in transfer function but Matlab has show the answer in continuous time state space model. 

 

The value of the transfer function : Gain = 58.46; Time constant = 0.55 and time delay = 0.06.

The value of Pi controller : Kp = 0.0784 and the Ti = 0.24. 

I had attach some picture which show the difference.

Am i did something wrong in the mathscript and should i do it in Labview by different way?

 

Thankyou very much 🙂

 

すべてをダウンロード
0 件の賞賛
メッセージ4/14
6,522件の閲覧回数

This is the regarding Labview file, could you please help me take a look?

 

Thankyou very much barp :).

0 件の賞賛
メッセージ5/14
6,520件の閲覧回数

Yuki

 

The problem is the delay from the First Order Model. If you look at the output error of "Unit Feedback Function", you will see a warning that says

 

Warning 41504 occurred at NI_CD_Model Interconnection.lvlib:cd_Feedback (TF and TF).vi

Possible reason(s):

Control Design and Simulation:  The delay information was ignored.

 

The main reason is that feedback function doesn't support delays. If you try to develop the model based on algebra, we can't represent the result as "exp (-D.s) *Num/Den".

 

To allow you to analyze such systems, you have two options:

1. Use Pade Approximation to obtain an equivalent model that of the delay and then, you can do the analysis as usual

ModelWithDelay.png

2. Use the function "Pade" in MathScript RT to convert the model. The command line is "Gp = pade (Gp, 3)";

 

This should allow you to analyze the model.

Barp - Control, Simulation, RTT and HIL - National Instruments
メッセージ6/14
6,494件の閲覧回数

thanks barp, thankyou very much, i had try out and it iss very useful for me, according to the previous graph u show me, there is a non-minimum phase behaviour occur in the response, i dont have zero on the right hand s-plane, but why the graph shown non-minimum phase behaviour? i mean it go opposite direction from the final direction. 

 

thankyou very much barp :).

0 件の賞賛
メッセージ7/14
6,454件の閲覧回数

Yuki

 

The non-minimum behavior comes from applying the pade approximation to convert the delay [exp (-0.06 s)] into a polynomial. For example, for order 3, the model has the following approximation:

pade_3.png

 

Which shows 3 zeros on the left side. If you increase this to 7, you will notice the pattern of zeros being formed on the left like this:

pade7.png

 

Here is the code related to this approximation, so you can 'play' with this code to understand.

 

padecode.png

 

Does it make sense?

Barp - Control, Simulation, RTT and HIL - National Instruments
0 件の賞賛
メッセージ8/14
6,442件の閲覧回数

Yuki

 

Just to be complete here. The reason you have to convert to pade approximation is because when you have a model with delay and you try to do the feedback loop operation, defined as:

 

Gcc = Gp*Gc/ ( 1 + Gp*Gc)

 

and you have a delay on Gp, you can't separated the exp (- Td*s) from the closed-loop equation and, in our toolkit, we can't use that. To overcome this problem, you can do the pade approximation we discussed above or you can try to use do nonlinear simulation. Then, you can develop the code as:

 

simulation with delay_simple.png

 

and you will see the response without the 'nonminimum phase effect'.

 

 