Error 61017

Solved!
Go to solution

Hi,

 

I am compiling a LAbVIEW FPGA code for a IF-RIO FPGA.

The code is compiled on a remote PC and then ported to a controller mounted in the same NI chassis of the IF-RIO board (by manually transferringthe LabVIEW project files).

Unfortunately, when I try to run it, LabVIEW returns the error 61017 and says that I must recompile the code.

 

In the past I was able to perform this operation without any problem, but now I have to recompile the code. Notice that the controller is much slower than the remote PC and this is the reason why I do not compile the code directly on the controller.

 

Is it a bug? Or could I have written some FPGA code that is somewhat changing when I tranfer the files?

 

Thank you

0 Kudos
Message 1 of 3
(7,901 Views)
Solution
Accepted by topic author tommpogg

Hi tom,

 

also read this…

 

First workaround: In the FPGA-Open node select the compiled bitfile instead of the VI (or build specification).

Best regards,
GerdW


using LV2016/2019/2021 on Win10/11+cRIO, TestStand2016/2019
Message 2 of 3
(7,897 Views)

Thank you GerdW, your workaround did the trick!

 

I have selected the compiled bitfile instead of the VI. The only problem is that I had to remove all the type definition controllers from the FPGA VI, since they were genereting an error.

 

0 Kudos
Message 3 of 3