How to Interface a sensor using IO-Link

Solved!
Go to solution

Re: How to Interface a sensor using IO-Link

LEHCR's approach is well worth trying. NI controllers, which have more than one Ethernet port, usually support EtherCAT. You can try to talk to IO-Link devices using an EtherCAT IO-Link terminal. For example: https://www.beckhoff.com/english.asp?ethercat/el6224.htm

 

Further more, it's highly encouraged and recommended to put your ideas on adding new feature here: https://forums.ni.com/t5/Data-Acquisition-Idea-Exchange/idb-p/daqideas 

 

 

0 Kudos
Message 11 of 17
(679 Views)

Re: How to Interface a sensor using IO-Link

The recent contribution to this topic brought to my mind that a while back I did solve my posted IO-Link problem successfully but that I never reported it here, sorry. In my case the solution was accessing the relevant information be reading the Modbus holding register value of the Comtrol IO-Link Master by simple LV TCP Write and Read functions. In fact I made a VI that reads the Modbus Holding Registers of a Comtrol 4-EIP Master to fetch the distance values of connected multiple Sick Laser Distance IO-Link Sensors of the type DT35-B15251. The achieved rate to get the distance values is rather impressive too.

 

I don't know if this is useful information at this point though.



Message 12 of 17
(664 Views)

Re: How to Interface a sensor using IO-Link

please, can you help me?. I need to see an example. 

0 Kudos
Message 13 of 17
(610 Views)
Highlighted

Re: How to Interface a sensor using IO-Link

OK I attach the VIs I made to access the Comtrol IO-Link holding registers that hold the distance data of the connected laser distance sensors from Sick. The Sick sensors are the type DT35-B15251 and the IO-Link Controller is the IO-Link Master4-EIP from Comtrol. I hope the information will help you to get started. The manufacturer of the sensor decides what data is provided, therefore you may need to adapt the VIs according to your needs. However, the basic scheme should be the same.



Message 14 of 17
(597 Views)

Re: How to Interface a sensor using IO-Link

Hi UrsL, I am new with labview and data comunications, please, can you help me?, I have a master AL1123 of IFM with flowmeter SV4610, how configurate the modbus in your VI attached?, can you explain more especific your example? or, can you say me an step by step?, please, help me.

0 Kudos
Message 15 of 17
(564 Views)

Re: How to Interface a sensor using IO-Link

Hi cridahe17,

 

Well, my VIs assume that the sensor is physically connected to the Comtrol IO-Link Master I mentioned and that the IO-Link description of the sensor is actually uploaded into the device. However, I don't know if this will work for the master/sensor combination you want to use. Depending on your particular master/sensor combination and if your IO-Link master has a built in web server, you should at least be able to access the sensor's data by your web browser once the sensor's IO-Link description was uploaded. Then you may use my VI as a template to go from there.



0 Kudos
Message 16 of 17
(522 Views)

Re: How to Interface a sensor using IO-Link

Hi UrsL,

 

I believe there are very few people like us who are trying to work on integrating IO-Link device with LabVIEW. Reading all the comments here, it seems like that your solution might help me in my project (after modification though). One small issue I am having is I have older version of LV.

Is it possible that you can save your labview project and all the VIs in the project for LV2014 and attach again here?

 

0 Kudos
Message 17 of 17