Hi George,
I hope you're doing well. To answers your questions in order:
1. The Watchdog Value (Boolean Value) is the actual boolean value that the DO module will output if the watchdog condition (network timeout) is met. What it sounds like you are trying to set is the period of time at which the bank should wait before going into this timeout condition. You can find this setting under the Device Configuration of your controller (FP-1000). There is a section called Network Watchdog Configuration, and there is a space to enter the Timeout in milliseconds.
2. The difference between the "enable" and "enable on use" settings is discussed in this KnowledgeBase [broken link removed].
3. The retry count field is defined in this KnowledgeBase as well [broken link removed].
Typically, these things will be defined in the FieldPoint Help (in your National Instruments folder from the Start menu), but I usually find the context help in MAX and searching KnowledgeBases the quickest way to get my questions answered. I hope this helps, George!
Thaison V
Applications Engineer
National Instruments