09-17-2013 12:33 PM
I have a sytem with 2 PXIe-1075 chassis' each having it's own PXIe-8133 controller along with multiple analog and digital I/O modules. There is also a reflective memory network installed using 2 GE Fanuc pmc-5565PIORC memory cards -one in each chassis. I'm using NI Veristand 2011 and currently I am displaying the Ring Read Late Count status channels for both controllers and they are both incrementing as long as the SDF is deployed. According to a NI white paper on distributed systems there should be no counts on these channels. There are a couple of configuration pages in Veristand (Reflective Memory Configuration and Reflective Memory Network Configuration) with little explanation of the settings or how they affect the performance of the RM network.
Is it possible to get information on how to properly set these up?
09-17-2013
08:37 PM
- last edited on
10-13-2024
02:18 PM
by
Content Cleaner
Not sure whether these are what you're looking for:
https://www.ni.com/docs/en-US/bundle/veristand/page/add-reflective-memory.html
https://www.ni.com/docs/en-US/bundle/veristand/page/optimize-reflective-memory.html
09-17-2013
11:34 PM
- last edited on
10-13-2024
02:18 PM
by
Content Cleaner
The late counts probably indicate a synchronization issue.
09-27-2013 11:23 AM
Do I need to have a chassis Master in both chassis' for hardware syncing?
Currently I have a DAQ card and FPGA in chassis 1 with the DAQ designated as the Chassis Master and no Chassis Master in chassis 2.
09-27-2013 11:31 AM
correct. you will need something to clock the 2nd chassis
09-27-2013 01:42 PM
A picture (screenshot) is worth a thousand words.
I get this error when I try to deploy:
Here are screenshots of controller and chassis setups:
Controller 1
Chassis 1
Controller 2
and finally, Chassis 2
PXI1Slot10 is a PXIe-6341 Multiunction DAQ
PXI2Slot6 is a PXIe-4300 Analog Input
Do you see anything wrong here?
Thanks for your help.
09-27-2013
02:16 PM
- last edited on
10-13-2024
02:19 PM
by
Content Cleaner
Thanks for the pictures.
The error is complaining one of your custom devices is not executable. Which device? The error doesnt show. Could be a missing driver or something.
You can leave your controller on automatic timing. That will pick DAQ automatically since DAQ is your chassis timing master.
Your start trigger configuration is wrong. You are exporting and importing a start trigger on RTSI/PXI_Trig lines which are internal to the chassis. That is incorrect. You must export/import from one DAQ card to the other.
09-30-2013 11:45 AM
Stephen,
Thanks for your reply.
As you suggested, I put my controllers back to automatic timing and then configured the start trigger export/import exactly like scenario 2 in the linked white paper. When I try to deploy, I get the following error:
09-30-2013 12:16 PM - edited 09-30-2013 12:18 PM
What is the error code?
what model of daq device is pxi1slot6? It might not have that terminal. Pick a different PFI by seeing what terminals the device has in MAX. If it has no PFIs then select a different card, one that has PFIs, as your veristand chassis timing master.
09-30-2013 12:16 PM - edited 09-30-2013 12:17 PM
Double post sorry
