08-15-2024 04:25 AM
I am new to using Veristand and PXI devices, so I'm having difficulty understanding an error message that I get when I try to deploy a Veristand configuration to our PXI system. The error message indicates our PXISlot17_AO device. When I look at this device in the System Explorer, I see that its name is bold and blue. I have no idea what this means. I assume that it is showing me some important status.
I have no idea where to start looking to fix this problem. Any suggestion on where to go look for the problem or what to read up to try to resolve it will be very helpful.
Somebody was working on our system and might have accidentally changed something to cause this problem. The Veristand configuration was deploying without problems before.
Solved! Go to Solution.
08-15-2024 05:35 AM
I believe I found the cause of the deployment error. There were two lines in the mapping diagram that were connected to each other.
The Veristand configuration is now deploying without any errors.
The PXISlot17 name is still in bold blue in the System Explorer. It would be great top know what this indicates.
08-15-2024 07:43 AM
@Hannes777 wrote:
The PXISlot17 name is still in bold blue in the System Explorer. It would be great top know what this indicates.
The bold blue indicates that the device is selected as the timing source of the master synchronization device. You can select a different timing source on the Chassis page.
08-15-2024 07:47 AM
Thank you very much for explaining that 😃