I`m running a SCXI-1162HV to gather some digital signals. At the moment the signals are all galvanic separated
and without power supply. How can I connect these signals to my terminal?
Do I need the galvanic separation at all?
Thanks for help...
0 Kudos
Messaggio 1 di 2
4.489Visualizzazioni
You should use galvanic isolation of input signals if
a) their voltage range exceeds the max input voltage of the DAQ system (you can use voltage dividers but these will not protect against excessive voltage spikes)
b) the reference ground of the input signals is at a level different from the ref ground of the DAQ system (the latter usually is the ref ground of the host PC which in most cases is connected to 'protection earth' of the mains outlet)
c) the ref ground are on the same level nominally but if there are long lines between the signal sources and the DAQ system which may cause level shift.