Modbus I/O slave commmunication status

Hi all, i'm using a cRIO as a modbus I/O slave (serial) to control some devices and sensors. I would like to implement a watchdog.

The watchdog will expire if there's no communication with the master for 20 secs, which will then reset the I/O to their default values.

 

I had a look at the slave modbus I/O addressing table:

 

 

Data Item Data Type Modbus Modbus Slave Description  
Read Write Read Write
               
CommFail Boolean value Yes No Yes No Represents a signal the Modbus I/O server generates. The signal is TRUE in the following cases:
  • Errors occur when the Shared Variable Enginefails to communicate with a Modbus device.
  • Errors occur on the serial ports or Ethernet interface of a Modbus Slave I/O server.
ErrorStatus 32-bit signed integer N/A N/A Yes No

Represents the error status of the Modbus Slave I/O server. If CommFail is FALSE, this data item is 0. IfCommFail is TRUE, this data item returns an error code.

Updating Boolean value Yes No Yes No Represents a signal the Modbus or Modbus Slave I/O server generates. The signal is TRUE while the Modbus I/O server polls a Modbus device or the Modbus Slave I/O server is being updated.

 

 

I created bound variables for the above. The variables work fine on the master modbus I/O. But it's always connected (CommFail = "F"), even when i unplug the serial cable.

And strangely, Updating is always "F" on the slave modbus, even when the values are being updated.

 