Hi,
I need to control the electric rods of a steam boiler and iam using NI PCI-6221 daq card.I have used K type thermocouple and giving its output to the channel AI at pin 68 and pin 34 of terminal block CP -68LP, after signal conditioning from instrumentation amplifier using IC tl084.But the channel is giving constant signal of 10 volts even i have not connected any input to the analog channel.Why is that so?....
02-15-2010 02:08 PM
Rather than setting this up as a voltage task, I would recommend doing a Temperature task. This will take care of a lot of these things for you. You should be able to directly connect your K type thermocouple to the pins on the CB-68LP and read the temperature. Also, how are you handling cold junction compensation? In the thermocouple task, you will have to select some type of CJC.
I hope you are able to get better results by setting it up this way.
Cheers,
Christina