Hello, I am using Labview 5 on a Windows 95 platform, and the hardware I have are the AT-MIO-16E-2 board, and the SCB-68 accessory with it. I am trying to read off a Druck PMP 1400 pressure transducer, with specs as below.
 
The problem I have is when I run the DAQ configuration utility. I run the test panels, with all the channels and devices configured properly, it still doest give me a reading which I expect. The outputs that i receive are in a waveform, but the values do not tally to that of my scaling.
 
The pressure transducer has outputs of 0-5V. I've connected the pressure transducer outputs to AI0 and AIGND channels in my SCB-68 box, selected channel #0 using a Referenced Single-Ended measurement system. Are these configurations correct?
 
My question is, what are the configurations that i need to put in the Channel Wizard? I hope i am giving all the information  that is needed. If there's anything thats missing from what you need to know, please let me know and i'll dig it up.
 
Druck PMP-1400 pressure transducer:
 
Thanks,
Jiawen
0 Kudos
Message 1 of 3
(3,049 Views)
Ah, problem sorted. I just had to put a jumper wire from the DC supply -ve as a ground wire to the SCB-68 box. Silly mistake. Sorry for taking up whoever's time who read this. Thanks.
 
Jiawen
0 Kudos
Message 2 of 3
(3,027 Views)

Your'e so (not) grounded, Mister!very-happy smiley

Glad you found the problem, happy sensing.

~~~~~~~~~~~~~~~~~~~~~~~~~~