I am using PCI 6602 to get continuous 1MHz square wave output from DIO1~32 sequentially controlled by LabVIEW. I used Ctr0 to generate a 2MHz clock and used Ctr0InternalOutput as the source of sample clock for DIO1~32. I attached the code and screeshots as follows.

The code is working fine on PCIe-6251 and the 1MHz digital waveform is very stable.

But when I run it on PCI 6602 I got an error -200077 (you have requested: sample clock; you can request: on demand).

Does PCI 6602 support hardware timing?. I didn't find information about this from its specs. If it doesn't support, how can I avoid this and get what I want? Thanks!

Yi

Version: LabVIEW 8.2

hardware: PCI 6602

0 Kudos
Message 1 of 3
(3,048 Views)
Solution
Accepted by happyeveryday

The PCI 6602 does not support hardware-timed digital waveform generation.  You can find this information on the product page or in the specifications document:

 

    23552i735FCDE544B250BC23554i4FE5DBFC693A869D

 

 

You can use the 8 counters of the 6602 to get 8 synchronized pulse trains, but clocking out arbitrary digital data is unfortunately not possible on this board.

 

 

Best Regards,

John Passiak
Message 2 of 3
(3,038 Views)

John, Thank you very much! Yi

 