Workaround for Watchdog on NI EVS-1463RT?

According to this KB article (http://digital.ni.com/public.nsf/allkb/2008A521FCE04E47862576D60058BE0F), Watchdog is not supported on the EVS-1463RT.

 

This is a major concern for a real-time system.  I have posted a product suggestion just now for this.

 

This post is to find out if anyone knows of any workarounds/alternatives to RT Watchdog?

Christopher Farmer

Certified LabVIEW Architect and LabVIEW Champion
DQMH Trusted Advisor
https://wiredinsoftware.com.au

0 项奖励
1 条消息(共 2 条)
2,500 次查看

Hey,

 

There are no "real" alternatives to a hardware watchdog, but you could toggle one of the available DIO lines. 

Then there are Timer-Relays which you could use to switch off the Power-Supply for the EVS when the DIO line doesn't change it's state anymore.

 

 

Thanks,

Christian

 