10-23-2021 02:52 PM
Hello Guys,
It is my first post/question, I'm trying the OPC UA toolkit with a PLC 1214C as a server, Id configured the PLC and I can connect LabVIEW to the PLC but appears an error Bad_NodeIdUnkown.
I'm just copying the Node ID created by the Tia portal as http://SiemensOPC;i=3 but it doesn't work.
I think the syntax is wrong but I'm new to this kind of communication.
Could somebody help me with this error, please?
11-02-2021 11:20 AM
Hello,
I was wondering if you ever got this issue resolved? I'm currently having the same "Bad_NodeIdUnknown" status when trying to write to a TIA Portal OPC UA server. Let me know.
11-02-2021 02:51 PM
Hey! I figured out the issue for me and I believe it will work for you. Please see my attached images for the NodeID format to be used for TIA Portal with LabView. Good Luck!