Patch LVRT2009f2

I installed the Windows patch as requested here, i also received a paper letter from NI about it, which says that affected devices are cFP-22xx, cRIO-901x etc. But one thing is not clear: what do i have to do on RT devices i already deployed before the patch? Installing the patch on Windows and recompiling RT executables is enough?
0 Kudos
Message 1 of 4
(3,160 Views)

Hi,

you are right, it is not so clear. Even in the readme file is not written.

I agree with you about re-deploying all executables after have installed the LVRT patch. This should be enough; but I will check and on the contrary _I will write you

 

Simo

0 Kudos
Message 2 of 4
(3,124 Views)
I just casually discovered that, at least for a cRIO 9014, if i go to MAX -> Remote systems -> (my target) -> Software -> Add/Remove -> Custom (not recommended!), there is a "VxWorks floating-point support" item described as the vulnerability fix. Certainly it's well hidden...
0 Kudos
Message 3 of 4
(3,092 Views)

You need only to install the floating-point support component to the target. You do not need to redeploy any Real-Time executables.

 

Cheers.

| Michael K | Project Manager | LabVIEW R&D | National Instruments |