I am trying to get and set temperature using this device using LabVIEW. I am able to communicate with the controller and it is responding to my write message. But when I try to say set a temperature of 28C, it sets it as 2.8C instead. Write command used is ":02064701001C94" to set 28C. Can anyone please tell me what am doing wrong? (code & manual (pg 17 attached)

 

http://www.dwyer-inst.com/PDF_files/E_90_CPC_rev4.pdf

 

0 Kudos
Message 1 of 17
(5,474 Views)

Try to send the command:

 

02064701011894

 

If this works then it would be because the controller is set to use one decimal. You need to send it a value that you can add a decimal to. It should be that easy. If you change the decimal setting in the controller it would change what you need to send the controller. This is what I have seen in the past.

 

I don't have that controller to prove what I believe is going on. To make your program flexible you will need to read out the decimal position and send the commands using that info.

 

Tim

Tim
GHSP
Message 2 of 17
(5,447 Views)

Hello Tim,

 

Thanks a lot! It saved my day.

Since you are familiar with this controller, could you also see if am doing anything wrong in the get vi? I am always getting a value of 51.2C when it is reading a temperature around 24C. Read string: "02032F020001C9", where "0200" is the value in hexadecimal which when converted to decimal and divided by 10 gives me 51.2C. Any ideas?

0 Kudos
Message 3 of 17
(5,444 Views)

OK first I think you are reading the wrong part of the response.

 

"02032F020001C9"

 

If I am reading the info you attached correctly you should be looking at "0001" section of the response:

 

"02032F020001C9"

 

Now the problem here is that I see the value of 1 when I do that. I am not sure what you are doing here. I have not used this exact controller before. I have used a controller from a different company that seems to act a lot like this one.

 

Tim
GHSP
0 Kudos
Message 4 of 17
(5,435 Views)

In the get vi, am writing a command to the controller ":020347000002B2" to read the temperature displayed on the temperature controller. Then am reading back from the temperature controller which gives back a command string "02032F0020001C9". If you refer pg 16 of the instruction manual attached, you will see "0200" is the "Content of start address 4700H". This is why I came to the conclusion that this is the part which contains the data. Let me know if you have any more ideas. (see you tomorrow)

0 Kudos
Message 5 of 17
(5,426 Views)

It looks like to me that you need to send this value:

 

020347000002B3

 

If you send this what do you see as a response? Also what is the temp when you ask for this?

 

 

Tim
GHSP
0 Kudos
Message 6 of 17
(5,425 Views)

Also try to send this and give me the values you are seeing and the temp:

 

020347000003B3

Tim
GHSP
0 Kudos
Message 7 of 17
(5,424 Views)
Solution
Accepted by topic author rv_labView

You commanded 2.8 C and got 2.8 C. The units (p.16) say .1C Multiply your hex number by 10. . . .

Message 8 of 17
(5,415 Views)

OK here is a vi that will calculate the command to the device. I would try to read 2 words and three words. This might be what the problem is. You are only reading two words at the moment. I would try to read three and see what we see.

 

Example.png

 

I realize there is an easier way to do this I just wanted you to see what I did to get to this value. It matches the document that you attached as reference.

Tim
GHSP
0 Kudos
Message 9 of 17
(5,408 Views)

OK I made a command generator using a ring. You can set the values and it will generate a command for each parameter. I also added an interpret vi. I don't have enough data to know if what I am doing is correct.

 

I would try to read the PV with one word.then 2 then three. This way we can try to see what the system is really sending since what you set me does not match to what they tell us to expect.

 

 

Tim
GHSP
0 Kudos
Message 10 of 17
(5,394 Views)