Floating issues on NI 9476 DO
I am using Ni 9476 Digital output module in Crio 9012 with 4 slot chasis, I am facing a wired problem with all the lines are in off state, i can read 8 vdc on each line across the ground terminal and also when i am trying to switch one line to ON State, it drives adjacent line to ON State. Someone Kindly help me to sort this problem.
Note: I have grounded the chasis, but the problem presist.
I have connected an external power supply to the NI 9476, the positive lead of the power supply to the supply pin, Vsup, and the negative lead of the power supply to the common pin, COM.
(5,007 Views)
Hi SVR,
did you read the datasheet of the NI9476? Did you look at the circuitry image?
 Those outputs are floating, when you switch off.
When you want to enforce low voltages in OFF mode you need to use resistors connected between each DO and GND…
(4,995 Views)
@GerdW wrote:
Hi SVR,
(4,985 Views)
Hi SVR,
what happens when you use a resistor of ~10kOhm between each DO and GND to avoid floating?
How does your schematic look like? What is connected to those floating DO channels?
How do you measure the voltage on those floating DO channels?
(4,979 Views)
Hi GerdW,
Kindly find the below answer for your question:
   The Floating Voltage pull down to Zero.
 I have connected all the channel to a relay of 24 Vdc, which drives solenoids, Contactor..etc
 Using Fluke DMM
(4,972 Views)
Hi SVR,
what happens when you use a resistor of ~10kOhm between each DO and GND to avoid floating? The Floating Voltage pull down to Zero.
That's the answer I gave you right from the start: use a pulldown resistor. And it's the standard solution for floating IO: use pulldown (or pullup) resistors…
(4,954 Views)
How much current does your relay need to operate?
Is the DO able to supply that level of current?
Offen a relay needs more current to operate that a normal DO can supply.
(4,948 Views)
