Hi Bing,
I would not recommend using an analog output module to act as a digital output module. Below is an excerpt from the c-RIO 9474 Operating Instructions manual and it sheds more light on the connectivity specification.
"The cRIO-9472/9474 has current sourcing outputs, meaning the DO terminal or pin drives current or applies voltage to the device to which it is connected. You can connect sinking-input devices, such as NPN, open collectors, normally high, IEC negative logic, or other DC devices to the cRIO-9472/9474. A sinking-input device provides a path to ground for current or voltage. Make sure the device you connect to the cRIO-9472/9474 meets the module specifications. Refer to the Specifications section for more information about the output specifications of the module."
02-07-2006 11:29 PM