03-30-2011 11:16 AM
I have no experience with Labview. I need to connect a third part opc client to get data from Labview 8.5. When I run the OPC Explorer and connect to the local server I see the data items. However if I run the free OPC explorer from matrikon it does not find any OPC servers. I see Variable Engine running in services. Lookout 6.0 is set at manual and is not running (I don't know if I need this). This computer is located in another country on the other side of the world and I only have RDP access. What am I missing?
Many Thanks
03-31-2011 12:42 PM
Hello,
Are you using the DSC module? With the DSC module you can add a 3rd party OPC client and bind your variables through that.
Here is a screen shot.