I haven't worked with the 8.5 DSC version yet. In the old days with the tag engine, the logging was done automatically once you setup the configuration to do it.
Here is the 8.5 info. Sounds like it happens when you create the shared variable.
Configuring Data Logging
When you add logging to a shared variable, the DSC Module logs shared
variable data, including the shared variable value, timestamp, whether the
value is in an alarm state, and the quality of the value. The DSC Module
logs all data to the Citadel database. Complete the following steps to add
logging for the Tank Level [Gallons] shared variable.
1. Right-click the
Tank System Shared Variables.lvlib project libraryand select
Edit Variables from the shortcut menu to open theMultiple Variable Editor
window.2. Double-click the
Logging:Enable cell for the Tank Level [Gallons]shared variable and select
On from the drop-down list that appears.Additional logging options appear as columns in the table.
3. Double-click the
Logging:Alarms and Events cell for the Tank Level[Gallons] shared variable and select
On from the drop-down list thatappears. This option enables alarm and event logging for the shared
variable.
4. Double-click the
Logging:Data cell for the Tank Level [Gallons]shared variable and select
On from the drop-down list that appears.This option enables historical data logging for the shared variable.
5. Double-click and enter
0.1 in the Logging:Data cell for the TankLevel [Gallons] shared variable. This value compresses the value to
one decimal point when the DSC Module logs the values of this shared
variable to the Citadel database.
6. Leave the
Logging:Deadband cell with the default value of 0.01.This value specifies that the DSC Module log the shared variable value
only when the shared variable value differs from the previous shared
variable value by 1% of the shared variable engineering scale range,
which is 0–100 by default