Flicker Measurements

I am trying to calculate short and long term flicker using my VI, image attached.

The values, Pst and Plt, are always zero and I don't know why.

I am reading the data that the scope acquired from a file.  It consists of time and amplitude.

Does anyone see anything, or many things, that I am doing wrong?

Thanks...

Flicker VI.jpg

 

 

0 Kudos
Message 1 of 5
(7,542 Views)

The Power Quality measurement VIs do not accept raw data input. You should resample the raw data first.

 

Please refer to the examples at:

C:\Program Files (x86)\National Instruments\LabVIEW 2017\examples\Electrical Power\Power Quality\Applications (DAQmx)\Flicker Measurement (DAQmx).vi

0 Kudos
Message 2 of 5
(7,521 Views)

Hi,

Is there an example of flicker calculation that does not require DAQmax?. 

thanks, Erez

0 Kudos
Message 3 of 5
(7,246 Views)

cRIO based example:

X:\Program Files (x86)\National Instruments\LabVIEW 201X\examples\Electrical Power\Power Quality\Applications (cRIO) (Delta-Sigma)

0 Kudos
Message 4 of 5
(7,229 Views)

Getting back to the flicker measurement... 

I'm trying to calculate the flicker, based on data I measured on a scope.

I can see that to get a valid value, I have to measure at least 10 min and break it to 200msec blocks . Is there a way to use a shorter data (for example, maybe zero padding or pure sinewave padding)?

Also, one of the inputs is the voltage range. There are only 2 options (230 and 120). My system is 400Volt. How should I converter the output?

thanks, Erez

 

Attached, a picture of the code (I replace the scope data by simulation)

thanks, Erez

 

erezg_0-1700333961668.png

 

 

0 Kudos
Message 5 of 5
(3,572 Views)