08-16-2012
12:55 PM
- last edited on
02-18-2025
04:55 PM
by
Content Cleaner
I'm trying to connect an instrument over Modbus to a CRIO 9074. I've gathered from searching online a couple of potential ways of doing this but I'm not sure.
1) One way that seems will work is using a NI9871 module. This seems pretty straightforward, however I will need to add this module to a 9144 EtherCAT under scan mode, will there be any problems with this? I will be spending quite a bit of money going this route.
2) Can I connect the Modbus from the instrument directly into serial port on the 9074 chasis?? This appears to be a valid route reading from http://sine.ni.com/nips/cds/view/p/lang/en/nid/201711. If it is, please tell me which pins on the DB-9 serial connection the T-, T+, R-, R+ from modbus connect to.
DB-9
Pin. Signal
1. DCD
2. RXD
3. TXD
4. DTR
5. GND
6. DSR
7. RTS
8. CTS
9. RI
Thanks in advance,
pd
08-16-2012 01:13 PM
paperduck,
The serial port on the 9074 is RS-232. Your pin descriptions sound like your instrument uses a RS-485 port. If that is the case then a simple ( inexpensive) rs485-rs232 adapter could be installed between the RS-232 port on the 9074 and your instrument.
08-17-2012 09:27 AM
Wayne,
Do I then use the visa vi's and parse them like a normal string over serial or is there another step involved in Labview? Thanks.
pd
08-17-2012
09:31 AM
- last edited on
02-18-2025
04:56 PM
by
Content Cleaner
I would start with the Modbus_lib for labview. It contains a set of modbus functions that use NI-VISA to communicate over serial or ethernet.
08-22-2012 03:28 PM
Wayne, thanks I've ordered that converter. The reason why I asked was because the equipment had the option to use RS-232 or RS-422/485 depending on jumper configurations for its output terminal. I configured it to output 232, but I'm not seeing anything on the RIO side.
08-23-2012 06:43 AM
Can you post the manual for the instrument?
04-02-2013 03:52 AM
I am facing a similar problem.
I would like CRio 9004 to communicate with a controller :
- using the Modbus protocol.
- using the crio's db-9 (de-9), rs-232 serial port.- knowing that my PLC (controller) communicate through rs-485 (2-wires protocol) or rs-422 (4-wires protocol) network.
Although I am starting to understand the "balanced/unbalanced problem thing",
I am still wondering whether there is a simple way to connect my device to the crio rs-232 port (I mean without using any rs232 to rs422/485 adapter) or not.
I think this won't work but still, can the following work?
connecting both my device's Rx- and Tx- to the db-9 Gnd pin5,
and Rx+ (resp. Tx+) to db-9 RxD pin2 (resp. db-9 TxD pin3).
(Thus without using DTR/DSR or RTS/CTS) ???
If this is feasible, what are the necessary conditions, voltages limits, ... ?
I hope this was clear enough, and thanks in advance for any answer or suggestion
NB : I just need to collect data from the PLC for further treatments (with others measures using crio modules)
NB2: I am French and I apologize if my English isn't good enough
Toriki.
04-02-2013 06:49 AM
Toriki,
You need an adapter. You can't connect a RS-485 port directly to a RS-232 port. RS-485 uses a differential mode of operation while RS-232 uses a single ended mode of operation.
These adapters can be purchased or you can build your own.
04-02-2013 09:03 AM
Thank you Wayne, although I hoped you would have told me that there's a simple way as I might use the rs485 network with maximum 2 slave devices.
Am I right if I think that using a rs485 - 4 wire network will be easier to implement/develop on LabView?
(Since there wouldn't be any need of sending/handling DTR/DSR (or RTS/CTS))
04-02-2013 09:54 AM
Just remember, you only need one 232-485 adapter.
There can be advantages to a 4-Wire ( Full Duplex) 485 network but most of the time a 2-wire is sufficient and probably easier to implement in LabVIEW. Typically a 2-wire 485 network has one master and many slaves. Master only talks to one slave at a time and slaves only respond to requests from the master. No handshaking is used.