Industrial Communications
取消
显示结果
搜索替代
您的意思是:
Version issue with ControlLogix - cRIO link (implicit messaging), "(Code 16#0315) Connection Request Error: Invalid segment type"
已解决!
转到解答
I developed and shipped a system to Germany several years ago.  It worked then.  But the cRIO was damaged and replaced with a newer model, and doesn't work now.  I suspect (and NI Tech Support agreed) it is a software version issue, which could be solved with NI-MAX software installer.  But I don't have access to the system myself, and correspondence is slow and tedious.
The original system was a cRIO-9073, developed with LabView 2009.  It used implicit messaging.  The Instance ID, sizes, IP addresses, etc. all worked great.
The current system is a cRIO-9074, with LabView Runtime 14.0 (I assume LV 2014), Scan Engine 4.3, NI-Industrial Communications for Ethernet/IP 14.0.0, etc.  The FPGA and CPU programs are loaded and appear to work in the cRIO.  The 'EthernetIP Set Assembly Instance Data.vi' returns no error.  But the PLC simply reports "(Code 16#0315) Connection Request Error:  Invalid segment type".  We've double-checked the IP (the error was different), sizes, and Instance #s.
The PLC has not be modified at all.
Does anyone know if there is any compatibility issue with LV-2014 and Ethernet/IP 14.0.0?  Or if there are any other packages required?
I'm including the NI-Max reports.
___________________
CLD, CPI; User since rev 8.6.
0 项奖励
1 条消息(共 8 条)
9,115 次查看
I have found reference to a mutli-cast/uni-cast issue.  Does the cRIO require an additional package to handle multi-cast ethernet?
I'm afraid I don't have a cRIO rack that I could experiment with.  So I can't even check the list of software options for NI-MAX to download into it.
___________________
0 项奖励
2 条消息(共 8 条)
9,110 次查看
According to below knowledge base-"NI-Industrial Communications for EtherNet/IP and LabVIEW Version Compatibility"
: https://www.ni.com/en/support/documentation/compatibility/16/ni-industrial-communications-for-ethern...
we can know that there is no compatibility issue with LV-2014 and Ethernet/IP 14.0.0.
And I think cRIO does not require an additional package to handle multi-cast ethernet.
Later I will set up the environment and investigate it more about the PLC error.
Wendy
0 项奖励
3 条消息(共 8 条)
9,054 次查看
I tried LV-2014 and Ethernet/IP14.0 and there is no problem communicating. I believe this must also have been verified before release.
There must be something missing here to see this error.
During the upgrading, did you format the cRIO device to install the new driver?
Have you tried having the new 9074 back to use the old LV-2009 driver?
0 项奖励
4 条消息(共 8 条)
9,026 次查看
Hi ZX81,
Can you get a copy of the wireshark capture file of their EIP communication?
0 项奖励
5 条消息(共 8 条)
9,025 次查看
The new system is on a brand-new cRIO rack (NI-9074).  The original was an NI-9073.
No, I don't believe they have any way to load LabView-2009 onto the new rack.  But I'll check if that is an option.
By the way, I had checked the compatibility matrix to see that LV-2014 and IndCom 14 are compatible.  But it didn't go into all the various packages loaded on the cRIO.  I've seen a few cases where the CPU gets loaded to 100% (not in this case), and packages just stop working or work intermittently.  I was hoping someone had experienced and fixed this before.
___________________
0 项奖励
6 条消息(共 8 条)
9,005 次查看
Re: wireshark
I'll see if that's an option.  This customer has very tight security rules, so WireShark may not be allowed.
___________________
0 项奖励
7 条消息(共 8 条)
9,004 次查看
解答
接受人 ZX81
Hi ZX81
In order to get you 2009 application to work with the new cRIO, you need to deploy it to the device. In order to be able to deploy the cRIO, you need to make sure it has the same software versions you used with the old cRIO.
You can format the cRIO from NI MAX and deploy the application from LV 2009. However, if you do not have access to the cRIO or your customer does not have the required software, you could deploy the applicaiton in another cRIO with the corresponding software (cRIO same model and same modules as your customer) and create an image from it and send it to your customer so he can deploy the cRIO even without the software in his computer. The next document explains how to do this.
RAD Utility
WenR
8 条消息(共 8 条)
9,002 次查看