RT Set time and EtherCAT

Solved!
Go to solution

Hi,

 

I have a NI 3110 Industrial Controller which controls several NI 9144 EtherCAT slaves. Due to the inherit drift of the clock in the controller I need to adjust the absolute time periodocally from the Windows-part of the program. I do this successfully using the "RT Set time and date" VI from the Real-time palette. However, after having adjusted the time on the controller, the 9144 chassis report an error 2147137804 - "Master is no longer sync'd with the slave device acting as the reference clock". To get rid of this, the only solution I found so far is to toggle the Scan engine mode from active to configuration and back to active.

Since this is not a good solution to the problem I wanted to know if there is a better one?

 

Thanks for any help,

Christoph

0 Kudos
Message 1 of 4
(6,816 Views)
Solution
Accepted by topic author fuchur

Open the ni-rt.ini on your RT target and find the following section:

 

[TIME SYNC]
source.ethercat.enable = TRUE
source.ethercat.usable = TRUE
source.ethercat.masterID = 0
source_priority = ethercat;

 

Change the first line
source.ethercat.enable = FALSE

 

This will make the slaves no longer synchronize to the first slave. Instead, all the slaves synchronize to the master clock. See if it helps in this situation.

 

DirkW

Message 2 of 4
(6,805 Views)

Hi,

 

thank you for the tip - I will try this as soon as possible. The master clock that you mention: is it the clock of the RT system on the Hypervisor?

 

Christoph

0 Kudos
Message 3 of 4
(6,798 Views)

yes the nanosecond realtime clock of  LV RT.

 

DirkW

0 Kudos
Message 4 of 4
(6,786 Views)