Hi,
I have a NI 3110 Industrial Controller which controls several NI 9144 EtherCAT slaves. Due to the inherit drift of the clock in the controller I need to adjust the absolute time periodocally from the Windows-part of the program. I do this successfully using the "RT Set time and date" VI from the Real-time palette. However, after having adjusted the time on the controller, the 9144 chassis report an error 2147137804 - "Master is no longer sync'd with the slave device acting as the reference clock". To get rid of this, the only solution I found so far is to toggle the Scan engine mode from active to configuration and back to active.
Since this is not a good solution to the problem I wanted to know if there is a better one?
Thanks for any help,
Christoph
Solved! Go to Solution.
11-28-2012 08:25 PM
Open the ni-rt.ini on your RT target and find the following section:
[TIME SYNC]
source.ethercat.enable = TRUE
source.ethercat.usable = TRUE
source.ethercat.masterID = 0
source_priority = ethercat;
Change the first line
source.ethercat.enable = FALSE
This will make the slaves no longer synchronize to the first slave. Instead, all the slaves synchronize to the master clock. See if it helps in this situation.
DirkW
11-29-2012 06:05 AM
Hi,
thank you for the tip - I will try this as soon as possible. The master clock that you mention: is it the clock of the RT system on the Hypervisor?
Christoph
11-29-2012 08:04 AM
yes the nanosecond realtime clock of LV RT.
DirkW