Aaron, are you there?...We are having important diferences between several environment temperature mesures, all done with FP-PT100 modules and OMEGA RT series 3-wire sensors. It looks like having a permanent offset of 6 or 7 celsius degrees at FP-PT100 modules. Example: Environment temperature mesured with conventional termometer is 25 degrees, and the value read with FP-PT100 through FP-1600 and FieldPoint Explorer is 32 degrees. Could you help us? Best Regards, Eduardo
Dear Steven, We have confirmed than almost all those modules are miscalibrated. We have measured -4,xx and -2,xx Celsius degrees like offsetts in two modules. By the same way, it is very important to know the exact length of cabling from PT100 sensor to FP-PT100 module, in order of adjust the final measured values. Question: Is it possible to calibrate the FP-PT100 2 wires modules in our laboratory? Best Regards, Eduardo