Digital I/O
Digital input behavior question
Hi Walter,
"port0" in the device test panel corresponds to the lines that are marked "P0.0" through "P0.7" in the PCI-6143 pinout diagram, not "PFI0" through "PFI9". (In other words, "P0.0" is short for "port0/line0".) The PCI-6143 supports using PFI terminals for timing/triggering signals, but it does not support using PFI terminals for DIO. Your USB-6211 does support using PFI terminals for both timing/triggering signals and DIO, which is why the terminals are labeled "PFI 0/P0.0" in the USB-6211 pinout diagram.
Also, port0 on the PCI-6143 has a weak pull-up resistor on each line, which will cause the lines to read high when they are configured for input and not connected to any external signals.
Brad
Brad Keryan
NI R&D
Message 11 of 14
(1,933 Views)
My terminology is wrong once again. I am not an electronic engineer. Whatever you call the lines, I have stated that in test panels, if you go to what NI calls digital I/O and hit start after selecting port 0, all lights indicating the individual lines stay high. If there is a slow 5v encoder signal going directly into PFI0 and port 0 is selected to view digital activity, what should you see on the screen?
1) I think you should see bit 0 blinking on and off. Bits 1 through 7 should remain off as there is absolutely nothing attached to them.
Is this correct? This is the way it worked last week.
2) This is not what I see. I see 8 lights that come on as soon as I hit "Start". They stay on as I turn the encoder. Not just the one hooked to the encoder but all 8 (7 of which are not attached to anything). Bit 0 light does not blink either.
Is this correct? This is the way it works now.
I don't know what the distinction is between digital I/O and timing/counting but this encoder is used solely for a reference pulse to trigger analog DA. It has worked in this configuration at speeds up to 5,500 RPMs or   66,000 pulses / second (720 counts / rev).
Message Edited by walter-donovan on 02-10-2009 12:44 PM
Labview 8.5
Meas Studio 2008
Message 12 of 14
(1,928 Views)
Accepted by topic author walter-donovan
Hi Walter,
Behavior #1 is correct for the USB-6211. On the USB-6211, the digital I/O circuits and the counter/timer/trigger circuits are connected to the same pins, which are labeled "PFI0/P0.0" and so on. This is a feature that the PCI-6143 hardware does not have, because the PCI-6143 is based on the older DAQ-STC system timing controller chip and the USB-6211 is based on newer M Series technology.
Behavior #2 is correct for the PCI-6143. On the PCI-6143, the digital I/O circuits are connected to one set of pins, labeled "P0.0" through "P0.7". The counter/timer/trigger circuits are connected to a completely different set of pins, labeled "PFI0" through "PFI9".
In addition, the USB-6211 and PCI-6143 have different digital I/O behavior when nothing is connected to the pin. The PCI-6143 has weak pull-up resistors, which pull floating (i.e. disconnected) digital input pins to the "on" state. The USB-6211 has weak pull-down resistors, which pull floating digital input pins to the "off" state.That is why the USB-6211 displays bits 1-7 as "off" and the PCI-6143 displays bits 0-7 as "on".
On the PCI-6143, if you want to be able to see the encoder in the digital I/O test panel (or in digital I/O tasks in DAQmx), you need to wire it to both "P0.0" and "PFI0". Then you should get similar results to the USB-6211 (except for the behavior of disconnected pins). However, if you only want to use the encoder as an analog input start trigger (or for counter/timer tasks), then you only need to wire it to "PFI0", not "P0.0".
Brad
Brad Keryan
NI R&D
Message 13 of 14
(1,919 Views)
Thank you Brad for your clear answer. This explained, I have checked the board and it is in fact receiving signals. MAX also seems to be running as intended. That leaves software. That's where we go next.
Labview 8.5
Meas Studio 2008
Message 14 of 14
(1,906 Views)
