SP7 toolkit and S7300 error 66

Solved!
Go to solution

Hello everyone,

We are trying to comunicate with the s7-300 (indicated below ). When we try to run the example "exmpl write_bit_array_in_DB.vi" an error 66 show up.
We comunicate correctly to the PLC and we are capable of make a "ping" from labview (with another example from labview).


We are wondering if it might be a configuration issue on the S7/300 that we are missing or maybe it is not possible comunicate with our hardware (CPU315-2DP+CP 343-Lean).

 

Thanks. 😉

 

 

Download All
0 Kudos
Message 1 of 3
(3,873 Views)
Solution
Accepted by topic author E.S.Mike

Hi,

 

i already answered you by e-mail.

For everyone else: For a S7-300 CPU leave Rack & Slot in "SP7 connect" on its default values 0 and 2 respectively.

 

Regards,

DATA AHEAD AG

Kudos are welcome...
Message 2 of 3
(3,778 Views)

Hello,

We started a new .vi (almost the same as the example) with the parameters and worked perfectly.

Thanks a lot.  

0 Kudos
Message 3 of 3
(3,771 Views)