09-19-2019 05:59 AM
Hello everyone,
We are trying to comunicate with the s7-300 (indicated below ). When we try to run the example "exmpl write_bit_array_in_DB.vi" an error 66 show up.
We comunicate correctly to the PLC and we are capable of make a "ping" from labview (with another example from labview).
We are wondering if it might be a configuration issue on the S7/300 that we are missing or maybe it is not possible comunicate with our hardware (CPU315-2DP+CP 343-Lean).
Thanks. 😉
Solved! Go to Solution.
10-14-2019 08:47 AM
Hi,
i already answered you by e-mail.
For everyone else: For a S7-300 CPU leave Rack & Slot in "SP7 connect" on its default values 0 and 2 respectively.
Regards,
DATA AHEAD AG
10-14-2019 09:48 AM
Hello,
We started a new .vi (almost the same as the example) with the parameters and worked perfectly.
Thanks a lot.