Dasylab sends only one string using RS232

Solved!
Go to solution

You can have one master and up to 15 slaves. However, if all of the responses have the "<" to start, then your current technique will not work.

 

Can you post your current worksheet file or make a small example with just the RS232 modules and the Action? 

 

The next step is to contact your reseller directly. This is not an efficient way to assist you!

 

 

Measurement Computing (MCC) has free technical support. Visit www.mccdaq.com and click on the "Support" tab for all support options, including DASYLab.
0 Kudos
Message 11 of 14
(3,731 Views)

Attached you find an example of the problem.

Each button sends a different command  to RS232.

This is only possible if you use 'restart on timeout' in options of the input module,

otherwise it will execute only the first pushbutton after programstart.

 

Regards

Andreas

 

 

0 Kudos
Message 12 of 14
(3,730 Views)

It is possible that you have not accounted for all of the characters.

 

Try setting the last command for 1x 5a $06\r

 

Let me know if that works. 

 

 

Measurement Computing (MCC) has free technical support. Visit www.mccdaq.com and click on the "Support" tab for all support options, including DASYLab.
0 Kudos
Message 13 of 14
(3,726 Views)
Solution
Accepted by topic author Andreas Graff

Yes, now it works as expected !!

 

Thank you very much !

 

Kind regards

Andreas Graff