PXI
PXIe-4461 using chasis PXI CLK10 as reference clock
I'm working with a PXIe-1062q Chasis and a PXIe-4461 ADC. I'm trying to sample a senoidal signal.
In Labview I9m using an example VI call "Continuos Output.vi". In this VI i'm having problems when i want to configure the reference clock, in the option "Timing Settings"
When I use the 4461 with his own board clock, the option "OnBoard Clock", the sampling it´s ok. But when I change for any option, for example "PXI_Clk10" (that's the clock of the backplane), ocurrs an error that I can't understand and I can't find in the NI page.
In the NI MAX the chasis and the 4461 are ok.
Thanks for your help, regards from Argentina.
(2,104 Views)
  1. You're selecting the sample clock in the Timing Settings section and not the reference clock, leave the sample clock as OnboardClock
  2. If you would like to configure the Reference clock, this example does not configure the reference clock and hence you need to add the following snippet to the example
  3. Note, you are using a PXIe chassis and a PXIe instrument, so the reference clock cannot be PXI_CLK10 but instead it should only be PXIe_CLK100 (type it in, you may not be able to select from drop-down)
Santhosh
Soliton Technologies
(2,074 Views)
santo_13, thank you very much for your response.
I've made the changes that you proposed to me. I've received the following error
I would appreciate if you send your ideas about the causes of this problem.
(2,064 Views)
Accepted by topic author LDParg
Just based on the 'SourceDevice' field, I assume that you've installed the 4461 on slot2 which is PXI only.
In this case, the reference clock has to be 'PXI_CLK10' and clk rate be 10MHz.
Santhosh
(2,048 Views)
It works! I'll change the ADC to the slot 5 and I'll probe the Pxie_Clk100 chasis reference. Thanks for the help!!!
I ask you one more question:
How can i set up the reference clock in the DAQ PXIe-6733? I have this device en the same PXI Chasis than the 6674t and the 4461.
I saw in the manual that i have to use the RTSI bus. In that case, the pag 14 of the 6733 manual says that the RTSI Clock is the PXI trigger (7) bus.
So, when i try to route the PXI_Clk10 to the PXI_Trig7 (or another PXI_Trig line occurs an error)
 And when I try to set up the time reference of the 6733 in labview occurs other error:
Could you help me with this?
Thank you very much!
(2,034 Views)
Firstly, santo_13 your help was very important. Thank you very much!
The question that I've written in this chat was solved.
Besides, i I've writen another question about the synchronization of the PXIe-6733. I've found the answer in that post
https://forums.ni.com/t5/PXI/How-can-I-synchronize-clock-on-multiple-PXI-devices/td-p/2222598?profil...
(2,023 Views)
