Multifunction DAQ
setting up loadcell with PCI-6229m, SCC-68 and SCC-SG24 module
Hi everyone,
I'm trying to set up different sensors in MAX/Labview DAQmx, using a NI PCI-6229 M-series DAQ-card with a SCC-68 connector block for measuring DC/DC-displacement sensors without SCC-module and measuring loads by using strain gage full bridges connected to SCC-SG24 modules.
DC/DC-displacement sensors:
I made a "voltage"-setup in MAX on an analog input of the PCI-6229 (e.g. ai4) with input signals from 0..5V. Then I defined a linear scaling (5V=100mm).
-> works.
Loadcell:
I was trying a "voltage with exitation"-setup, because of I connect the strain gage signals to a SCC-SG24 module. At maximum load the sensor signal ist about 2,5mV/V. So, with 10V exitation voltage i'm getting a maximum Signal of 25mV. When I multiply the fixed gain of the SG24-module of 100, I get 2,5V as result. So, my signal should range from -2,5V to 2,5V. When I try to type this into the min/max setup form, I always get the error, that the maximum range is +-0,1V???
-> Do I have to type in the signale range without 100x gain?
Thanks for your help.
Tom
(3,078 Views)
Hi Tom,
The Input Range is the Physical Input Range of the SG24 and it's -0,1 to 0,1 Volts.
The Software know that SG 24 give an Gain x100 and make is own conversion.
Best Regards
Matthieu Papaux
Applications Enginneer
NI Germany
(3,062 Views)