Multifunction DAQ
cDAQ 9174 with 9203 current input module
[New to compact DAQ]:   In order to use the cDAQ 9174 with 9203 current input module - Is a separate external power supply required for the 4-20mA transmitters for which you want to read, or is this power provided by the chassis/module?
To connect 8 single-ended 4-20mA transmitters to one 9203 module, is there an external terminal block required to connect all COM inputs?
(3,198 Views)
Hi Michael-j,
This is from the 9203 Manual so if your transducers do not supply their own power you will need to give them a voltage source to source current from.
22022i465E9C0C0E506241
If you are connecting you may want to use a ferrule to connect multiple wires, or a terminal block if you are using the above configuration.  Post back if you have questions.
Regards
Dustin D
(3,188 Views)