12-10-2023 01:55 PM
I have connected two red and wire terminals from 24 VDC step down transformer to corresponding red and black wires from Belimo actuator. I have connected orange wire from the actuator to NI DAQ 6212 Analog Ouput A01 and AGND. My LabVIEW program is attached herewith. I am not able to open and close the control valve when temperature exceeds certain limit. I have used DAQ 9212 and K type thermocouple for temperature measurement. Please can anybody solve this problem. What is wrong with my wire connection? I think it is correct in LabVIEW.
Thank you.
Solved! Go to Solution.
12-10-2023 05:39 PM
Are you sure you've TFRB24?, the datasheet shows only two wires and no control signal.
12-11-2023 09:48 AM
Hi. Thank you for the reply. It is TFRB24-SR.
12-11-2023 10:07 AM
User manual - https://www.belimo.com/mam/general-documents/datasheets/en-us/belimo_TFRB24-SR_datasheet_en-us.pdf
Looks like you've connected the Orange wire to AO GND whereas it is your feedback signal from the motor and you missed to connect the GND together.
12-16-2023 02:48 AM
Thank you for your reply. I tried to reconnect the wire as per your suggestions. Please see the attached pictures. But I am still facing the same issue of being unable to control the valve's opening and closing. I don't know what mistake I made with the connections. Could you please take a look and find my mistake? Thank you.
12-16-2023 10:32 AM
It would be better if you had listed the connections you made instead of having me to search for pinout and look at images to figure out the connections.
For sure, you need to make your wiring better or pretty soon you will regret after blowing things up.
12-20-2023 09:57 AM
Thank you for the great help. It is working now.
12-20-2023 10:23 AM
@anis77 wrote:
Thank you for the great help. It is working now.
It's good that it is working now, so what changed between your last comment and this one?
Please don't forget to mark the appropriate post as an answer if it helped answer your question.
12-20-2023 10:50 AM
The connection you had suggestion was correct. I had used voltage range 3-6 V, so even it was working, i could not see the opening and closing of the valve. I increased the range from 2-10 V, now , it seems, it has wider openings.