Multifunction DAQ
NI 9203 current sensing module
Hi I have a 9203 module that's is a current sensing module and it's an 8 channel module, I am measuring a 4-20 ma pressure transducer from a compressor which is in this module and works perfectly in Labview, and I would like to have a different device, measure that same current and effectively Y splitting the cable. How can I do that?
(3,309 Views)
Hi jehad10,
Here is a good document that explains and gives examples on how to set up transducers and devices in a 4 - 20 mA current loop:
Fundamentals, System Design, and Setup for the 4 to 20 mA Current Loop
https://www.ni.com/en/shop/data-acquisition/fundamentals--system-design--and-setup-for-the-4-to-20-m...
Splitting the line would represent a current division, which would not preserve your readings, however you can boost the voltage of your power supply and connect the two devices in series (see Figure 6) to ensure that the loop is still receiving the power it needs.
Jorr-El
Systems Engineer
Testeract: Automated Test Specialists
(3,262 Views)
