Brian's suggestions hit the mark. One item to be careful of is if any of your mechanisms will 'run away' with loss of drive power. This is typically the case for ballscrew-driven Z axis stages. Under loss of power, gravity may pull them downwards. If this is the case, the stage should have a brake mechanism that is active when unpowered.
Normally closed contact is typically the norm since it is failsafe operation if the wires get cut or connections open up.
11-28-2005 03:44 AM
11-28-2005 11:33 PM
Than you all for your contributions.
The shut down option is close to what I need. However, i need to drive four independent and otherwise dupplicate systems with the four axis of the 7344 motion controller. At any given time only one of the axis might have an emergency stop activated. If that is the case than only the respective axis shuld be shut down not all four axis since thie will cause interference with four production line and therefore becomes expensive.
The double use of limit switches of a given axis might be another option, however on direction of the motion uses the limit switch as a home switch and it still needs to be active indepentend on the emergency stop function.
Thus my revised question is, how can the 7344 be used for four independent dupplicate systems, each with their respective E-Stop funtion?