03-17-2012 05:16 AM
Setting camera parameters by Pylon software didnt give the desired result too. i tried both line 1 & 2 but didnt work all tries gave a continuous capturing
03-17-2012 06:06 AM
Then there might be problem in your camera I/O Board. Try to replace with other camera and check it what will happen.
03-19-2012 12:43 PM
03-20-2012 04:42 AM
These are already the lines I use for external trigger
03-21-2012 12:14 PM
Hi Frank,
Have you been able to verify with a DMM that the trigger is actually sending a pulse? Are you able to connect the camera directly to the computer and try to verify that the trigger is working? Do you have another camera that you can try to set the trigger up on so that we can eliminate the camera as a problem?
Thanks,
Kira T
03-22-2012 02:05 AM
i tried using terminal block again and it takes two frames per trigger and that some how satisfied but it doesnt work the same when i directly trigger the camera from PLC
NOTE: output pulse from PLC to terminal block to make output from terminal block to camera
03-23-2012 10:59 AM
Hi Frank,
Can you post a screen shot of your settings in Measurement & Automation Explorer? When you are triggering directly from the PLC, how are you wiring the system? Are you able to verify that when you do not go through a terminal block you are producing a signal?
Regards,
Kira T
03-25-2012 06:27 AM
that`s a screen shot of settings
i directly take PLC out to camera or through interface relay.
the plc out i program it as i wish and i verify it
03-26-2012 04:40 PM
So what is the exact signature of the signal that comes out of the PLC, versus the one that comes out of the terminal block? How high does the voltage go for each?
04-03-2012 03:28 AM
The PLC gives 24 DCV pulse its width controllable.
the terminl block gives 5 DCV pulse its width uncontrolled.
i lowered down the PLC voltage output by using resistor but didnt work.
Can you tell me what is the best hardware connection when i trigger the camera directly from the PLC?