12-03-2009 08:20 AM
Hi,
I am using modbus library to control a Lumen temperature controller. The controller is connected trough RS485. I am using a FTDI chip with VCP driver to interface this component.
The modbus transfer is in RTU mode.
On each step :
I am reading the temperature on a device's register.
I am writing relay set point depending on time and consign.
My program is working fine during one hour (sometime 2 or 3 hour). next I have this error :
Error -1073807194 occurred at VISA Write in MB Serial Transmit.vi:7->MB Serial Master Query.vi:6->MB Serial Master Query Read Holding Registers (poly).vi->read-register-safe.vi->boucle-temp.vi
Possible reason(s):
VISA: (Hex 0xBFFF00A6) The connection for the given session has been lost.
This error occurs during a reading period.
I attache the VI :
Boucle-temp-safe is the main program.
Read-register is the sub program generating this error.
I hope you could help, i am using this program to control the temperature cycle when i press ski (handmade ski build with friend). I have to set the set point manually for the moment.
12-03-2009 11:13 PM
12-03-2009 11:15 PM
12-17-2009 06:46 AM
Hello,
I think i solve my problem.
My usb transducer was buy on ebay with a ftdi chip.This transducer isn't stable in time (2-4hour).
I buy a new ftdi transducer on ftdi web shop and now it seem to work (22h). I have to test it on a longer period.
Thank you for help.