Hi Ahemer. A couple of questions:
1) Are you using shielded cables to the RTD sensors? Grounded only at the cFP-RTD-122 end? How long are your wires?
Any connections in the wires, other than at the CB-1 and the sensor?
2) Are you seeing only long term instability now? It sounds from your post like you did see some noise (short term
instability) but that was resolved with the power supply ferrite.
3) Is the backplane well grounded (grounding screw on the bottom, below slot 2 on a 4 slot backplane)? Power supply grounded?
4) Are you taking readings from MAX, are the temperatures stable there?
5) What production revision of the cFP-RTD-122 do you have (letter code in the part number, i.e. 185078D-02 is
a revision D)?
Matt