Storing 32-bit numbers in plc registers.
I am using Labview 7.1 and DSC/OPC to communicate to an Allen Bradley SLC 5/05 over Ethernet. In my application, I desire to write and read part numbers ranging from 0-99999999 to/from the N registers of the PLC. Now since the N (Integer) registers of the 5/05 can't store a value of 99999999 I attempted to use the split function and store the value into (2) seperate N registers. Then I could take those two registers and use the join function to re-establish the value when reading. What happens is, I will write one value and read something back totally different. If the lower word is greater then 32767 when split, I have bad results.
(3,063 Views)
Chilly Charly    (aka CC)
(3,043 Views)
(3,043 Views)
Sorry for the blank posts, just an accident !
Now I feel obliged to give some answer...
Display the results in Hexadecimal format and see if your problem is not due to byte inversion.
CC
(3,042 Views)
"IF the lower word is greater then 32767 when split, I have bad results"
You don't say what OPC you're using, but if it's one of the Industrial Automation/Lookout drivers for AB that came with LVDSC, here's a guess what the problem is:
With a 32bit input, the split function results in two U16 values. A quick check of the IA/Lookout documentation for the AB drivers shows that N registers data members are configured to accept 16 bit _signed_ integers (-32768 to 32767). When you try to write 0x8000 as 32768 to your lo word tag/register, DSC/OPC just coughs.
Suggested possible solution:
Typecast the lo word U16 from your split to I16 and write that value to the tag/register.
If you're using another OPC driver, the problem is probably something similar.
Fading out. " ... J. Arthur Rank on gong."
(3,026 Views)
