01-24-2013 07:51 AM
My DAQ system includes RTD temperature measurement via a NI9219 module. The usual analog in (NI9201), analog out (NI9264), digital in, digital out (NI9401) work fine and run adequately with a single software timed while loop at 20 msec per iteration. When I add the temperature inputs the loop slows down to the 2 Hz rate of the NI9219 - fine for the temperature measurements but too slow for the user interface and the rest of the system. How can I keep the loop running and only update the temperature data when the NI9219 finishes?
Solved! Go to Solution.
01-24-2013 07:55 AM
Use a case structure so that you read the temperature every 25 iterations.
I would recommend keeping the count in a shift register. Each iteration increment and use the Quotient & Remainder to get the remainder of the iteration number and 25. When the result is 0, read the temperature. Put the remainder into the shift register.
01-24-2013 08:36 AM
Thanks for the quick reply. It will take me a bit to implement the case structure and I don't think it will work. The problem, as I understand it, is that LabVIEW blocks other conversions and updates while the NI9219 performs a conversion. What I believe I will see with your suggestion is half a second of updates followed by a frozen half a second while the NI9219 does it's thing. Is that what you were expecting? If so, it is no more acceptable than updating everybody at the NI9219 rate.
What I think I need is some way to start a NI9219 conversion. Continue LabVIEW processing, polling the NI9219 for conversion complete. Upon completion collect data and start over. Unfortunately, I don't see the tools to do that.
01-24-2013 08:51 AM
How are your tasks setup? If you are doing continuous aquisition, then it will be constantly getting the data at a given rate in the hardware.
01-24-2013 08:52 AM
I do not know anything about the NI 9219 but it sounds like you should look at a parallel loop for the slow acquistion. Something adapted from the Producer/Consumer (Data) Design Pattern should work. You might need three or more loops so that all your hardware tasks are isolated from the data analysis and GUI.
Lynn
01-24-2013 10:30 AM
Thanks to both of you for your help. Lynn, your response put me on the right track but I don't need the Consumer/Response Design. What I needed is three while loops. One for the slow sensors (NI9219), one for the fast sensors and user interface, and a third around both. Now LabVIEW starts the slow acquission and then lets the faster acquission run. I still have a lot of clean up to do but that is the easy part.
Again, thank you both.
Bill
01-24-2013 10:32 PM