Hello!
I faced a strange behavior in LV2023Q3 creating real-time shared variables. There is no option to turn on RT FIFO. Here's how it looks on a PC running LabVIEW 2020 SP1 - more options for variables, and RT FIFO among them. And a significantly shorter list in LabVIEW 2023Q3 with no RT FIFO at all. Everything necessary is installed (I use an academic license with full set of modules included). And I double-checked on two different PCs - same thing. What could be the cause?
10-26-2023 02:52 AM
Same for me, any progress on that?
10-26-2023 08:49 AM
It looks like you have the LabVIEW DSC and Real Time modules installed on LabVIEW 2020 SP1. That is why you see the extra items for the Shared Variables.
03-21-2024 12:34 AM - edited 03-21-2024 12:35 AM
Hello amayzel2
Not sure if you've already solved this but just in case someone encounters this same problem:
This is a bug from LabVIEW 2023 Q3 Patch 1 and was solved in LabVIEW 2023 Q3 Patch 2. You can go to the NI Package Manager and select LabVIEW 2023 Q3 and it should install the Patch 2 and fix the bug.
Source: https://www.ni.com/en/support/documentation/bugs/23/labview-2023-q3-bug-fixes.html
03-24-2024 06:20 PM
You show that your Real-Time Target is a myRIO. Have you installed any version of the myRIO Software Toolkit? As far as I know, the two most recent versions are myRIO Software Toolkit 2019 and myRIO Software Toolkit 2021. Do you have any myRIO support installed on your LabVIEW 2023 system?